bcl
Member
- Location
- Garden Ridge, TX
- Occupation
- Electrician (Owner/ Operator)
1. Generac makes a cable for backup generators that integrates the feeders and control wires into one cable. It consists of Three #3AWG - One #8AWG - Six #18AWG (copper). This cable is meant to be used for generators rated 16-24 kW, protected with a 100 amp breaker (there are smaller versions as well for smaller generators). It is a fairly common product made by multiple manufacturers, although many electricians don't seem to know about it. I also see lots of electricians insisting that you must use #2 AWG for 100 amp feeder. I'm guessing that most of the time this is because they are not paying attention to 83% rule in 310.12(B). Am I thinking through this correctly?
2. My question also pertains to the bundling adjustment factors in 310.15(C)(1). My first thought was that they would have to be applied because of all the wires integrated in one cable. 11 wires would be 50% adjustment factor. Making those adjustments would make it impossible to use #3 copper for the 100 amp feeder, but I guess the control wires, even though they measure 240v, are not considered current carrying conductors because their only purpose is for monitoring voltage. I have not tested these control wires for current. Am I correct on this, or is there some other code that I'm missing that makes this cable an acceptable installation according to the NEC (even though AHJs may not allow it)?
2. My question also pertains to the bundling adjustment factors in 310.15(C)(1). My first thought was that they would have to be applied because of all the wires integrated in one cable. 11 wires would be 50% adjustment factor. Making those adjustments would make it impossible to use #3 copper for the 100 amp feeder, but I guess the control wires, even though they measure 240v, are not considered current carrying conductors because their only purpose is for monitoring voltage. I have not tested these control wires for current. Am I correct on this, or is there some other code that I'm missing that makes this cable an acceptable installation according to the NEC (even though AHJs may not allow it)?