keith gigabyte

Senior Member
Looking for information on a 60kw 120/208 3 phase generac generator. generator sat for 1 to 2 years onsite, never exercised or transferred load.
obviously had dead battery, replaced that. now it cranks on or 2 revolutions and throws a rpm sense loss fault. from what I can find online there is a flywheel sensor and possibly feedback from the ignition coils.
Generac is kinda closed mouth when it comes to info. any input on this issue would be appreciated.

thanks
 
Does this set have a control panel with an LCD display and a key switch control? Sometimes the control panel will lose its programming and revert to default numbers that don't match your hardware. I have a client with an 80 kW set which I've had to reprogram the data twice and send in the panel to flightsystems.com two other times. Programming data on this set was glued to the inside of the control panel lid and also in the owners manual. One of the parameters to set is the number of teeth in the flywheel for the flywheel sensor to correctly count RPM.
 