Series of questions about whole home generators given a 14KW generator.
Example 14kw generator so roughly a 240v 60amp
Conductor size 445.13A 60 x1.15=69amp so assuming 75c terminals copper#4 rated 85amps.????
Part 2 For example house currently has 120/240 single phase 200amp service.
load calc for house actual is lets say 120amps. Would you by code be required to get a larger generator if using whole house transfer switch or would it be up to user to limit their load.