But are they talking the individual grounded counductors or the #4 grounded conductor. My thought is the #4 would be sufficient enough. In the instructions I have it shows it done both ways
From the instruction manual. read the
note.
12b. In the main panel, remove the black (hot) wire from
the circuit breaker that protects a circuit to be powered
in the event of a power failure. Wire nut the black wire
to the matching circuit lead wire from the emergency
circuit breaker in the load center in the transfer switch.
(All circuit wires are color coded and labeled for easy
identification). UL listed wire locknuts are included in
installation kit. Trace each black (hot) wire connected
and wire nut the white (neutral) wire from the same
Romex cable (circuit) to the matching circuit number
on the white (neutral) wire from the emergency load
center. Repeat for each circuit. Repeat this process
with the remaining circuits to be powered by the generator.
NOTE:
Both grounded and ungrounded conductors must be moved
to the emergency panel and connected to the new wiring
from the emergency panel using supplied wire nuts.