Marcus11
Member
- Location
- Boulder creek ca
- Occupation
- Electrician
Iv recently installed a 7.5 powerpact for a customer that has only 120v to the main panel from the utility. I hooked up the generator and automatic transfer switch like i have done in the past. In the main panel there is a jumper allowing 120v on both bus bars. i have, feeding into the transfer switch two conductors that have 120v on them but they are from the same source so its nothing when i go across both of them, but i do get 120v to ground across both legs, when tested individually. When i shut utility power off like im mimicking a power outage the generator starts and transfers the load, the problem is when i restore utility power the generator or the transfer switch doesnt sense that power is restored and just keeps running with the load transfered, i have to manually stop the generator. The fuses are all good and control wireing it triple checked. My question is, if the transfer switch or genset needs to sense 240v to turn off and is the problem that there is only 120v coming in from the utility. Any help would be greatly appreciated, thanks.