skorpioskorpio
Member
- Location
- Georgia
- Occupation
- Engineer
I had my Generac generator installed by a generator company, and something seems very wrong with their installation. It is using a 16 space/24 circuit sub-panel layout fed from a 100 amp breaker from the main panel (not a whole house switch). I noticed that there is only a single neutral/ground bar in the switch panel, which they have connected both neutrals and grounds to. Why would this be? Shouldn't there be separate ground and neutral buses? The panel uses Siemens guts and there is a place to snap in a 2nd bus rail, but it isn't there, just the one. There is also no place for a can mounted bar, just the snap in spot where on a regular Siemens panel would have a secondary neutral bar. Does this switch not follow the rules of a sub panel where ground and neutral should be unbonded?
The generator itself has a feed breaker, and the switch has no manual disconnect (it is fused though), I don't see anyway, or any scenario where this switch could be viewed as the first point of disconnect where neutral/ground bonding would be appropriate. It just seems very wrong. Seems like there should be a 2nd bar to separate the grounds from the neutrals and that the ground bar should then be bonded to the can, right?
The generator itself has a feed breaker, and the switch has no manual disconnect (it is fused though), I don't see anyway, or any scenario where this switch could be viewed as the first point of disconnect where neutral/ground bonding would be appropriate. It just seems very wrong. Seems like there should be a 2nd bar to separate the grounds from the neutrals and that the ground bar should then be bonded to the can, right?