General 120v duplex recept

Status
Not open for further replies.

TTwizted

Member
Location
florida
I installed a regular duplex recept, and when I put my plug in tester it says the neutral and hot are switched. Mind u that I have been an electrician for over two years and in school going on my last two years to be a certified electrician lol. So that being said, I know how to wire a recept. I found a jbox in the attic so that's where I jumped the power from. Anyway the weird thing is it is good when my kitchen lights are off but when I turn them on it makes my neutral hot along with my hot still being hot. What could this be?
5b17eb3e93e847a870668aeee153689b.jpg
af714cabc2371ebf568e7cd03da96b5a.jpg



Sent from my iPhone using Tapatalk
 
You probably connected to a switch leg or a traveler of a three way which uses a white wire and was not taped or painted black.

Sent from my XT1585 using Tapatalk
 
Welcome to the forum. You need to check with a multi-meter to see what's truly going on. Plug testers are ok but have a lot of limitations. I had one tell me I had an open neutral when in fact the breaker was shot and only allowing ~40V thru.

If you truly have hot-hot, you either have 0V across hot and neutral, and nothing plugged in will work, or 240V, in which case it'll work really well for about a second before it goes poof.
 