General Duty or Heavy Duty Disconnects

Status
Not open for further replies.

norcal

Senior Member
Me thinks it's voltage dependent, 480,600V is HD only, general duty is 240V max, so job specs or how competitive the bid is.
 

kwired

Electron manager
Location
NE Nebraska
In these parts general duty is nearly non existent. You may find more in the 30 amp 2 pole 250 volt category but most everything else is always heavy duty.
 

iwire

Moderator
Staff member
Location
Massachusetts
From Square D.

What is the difference between a general duty & a heavy duty safety switch?


There are many differences between a General Duty and Heavy Duty safety switch: maximum voltage rating (240Vac vs. 600Vac/600Vdc), maximum amperage rating (600A vs. 1200A), maximum short circuit current rating (100KAIC vs. 200KAIC), NEMA Type enclosures (Type 1 and 3R only vs. Type 1, 3R, 4, 4X, 5, 7, 9, 12, and 12K), for instance.

In general, General Duty switches are intended for residential and light commercial applications, while Heavy Duty is intended for commercial and industrial use. The Heavy Duty switches have a wider variety of accessories available. Per NEMA standards, Heavy Duty switches must be provided with a dual cover interlock.