In nearly every explanation of Table 220.42, I see people indicating that general lighting that does not fall under dwelling units, hospitals, hotels/motels, or warehouses should have a 125% demand factor applied for continuous loads. I never see the same 125% factor applied to the first 3000VA of dwelling units or the first 12,500VA of warehouses, despite these having the same 100% demand factor within Table 220.42 as the last line of "All Others". Why is it that the continuous loads factor is applied in this seemingly inconsistent way?
Who is to say that a specific other load will certainly be on for more than 3 hours or that a listed load will not? In addition, the continuous load definition is that of a load where the maximum current is expected to continue for 3 hours or more. In an age where the prevalence of easily dimmable LED lighting has made it so that lighting will usually be dimmed and therefore not pulling the maximum current, can we even assume that lighting falls into the continuous load definition anymore?
I'm a new PE trying to wrap my brain around what seems like a disconnect to me in how we as an industry apply this demand factor. Thanks in advance for your help.
Who is to say that a specific other load will certainly be on for more than 3 hours or that a listed load will not? In addition, the continuous load definition is that of a load where the maximum current is expected to continue for 3 hours or more. In an age where the prevalence of easily dimmable LED lighting has made it so that lighting will usually be dimmed and therefore not pulling the maximum current, can we even assume that lighting falls into the continuous load definition anymore?
I'm a new PE trying to wrap my brain around what seems like a disconnect to me in how we as an industry apply this demand factor. Thanks in advance for your help.