How do you know the transformers are bad? I believe your fuses are too small. Often times the highest inrush on a small transformer (i.e. control power) is when it is energized no-load.
A single phase 2KVA transformer with a 480V primary would have a continuous current draw of 4.17A. In general for small transformers, many fuse manufacturers recommend sizing the primary fuses starting at 175%, so in your case this would be a 7-1/2A time delay/dual element fuse.
Per the NEC, to use a fuse this large (more than 167% but less than 250%) on the primary would require the transformer to have secondary protection, in your case this could be a 20A fuse or breaker.