General purpose transformers in Class I, Div 2 locations

Status
Not open for further replies.
I'm trying to determine if installing a 45kVA General-purpose low-voltage dry-type 3-ph transformer (such as the SquareD EX45T3HCU) in a Class I, Division 2 (Groups C&D) would be a code-violation. The transformer is a 480V delta primary, with a 208Y/120V secondary.

NEC 2011 501.100 (B) points to 450.21 through 450.27.
Using the 45kVA transformer that I linked, 450.21 seems to indicate that there is no restriction as long as my transformer is "completely enclosed, with or without ventilating openings". I do not read this as being a sealed encapsulated transformer, but I could be wrong. Would you say that the linked transformer does not violate the code, and therefore can be installed in a Class I, Div 2 area?

I have asked a couple of major electrical manufacturers this question and received their answer, but I don't want to overly bias the conversation before hearing your thoughts.

Thanks.
 
What 501.100(B) is telling you is that Class I, Division 2 adds no restrictions beyond those already in Article 450. If installed as would otherwise be required under "ordinary locations" the transformer you linked to is fine.
 
On the other hand, I would imagine that something other than a general purpose transformer, such as one with an automatic (or even manual switch?) tap changer for voltage correction might not be OK?

Sent from my XT1585 using Tapatalk
 
On the other hand, I would imagine that something other than a general purpose transformer, such as one with an automatic (or even manual switch?) tap changer for voltage correction might not be OK?

Sent from my XT1585 using Tapatalk
Those items fall under Section 501.115(B). The transformer itself is fine.

EDIT ADD: In fact, Section 501.115(B)(2) has some interesting material about isolating switches with respect to transormers.
 
Thanks for the responses! I had asked 2 manufacturers and both claimed that if installing the transformer in a Class I, Div 2 environment, the transformer had to be a sealed resin-encapsulated transformer (at increased cost). The sealed transformer has a CID2 rating, but I'm not sure that's relevant. I understand that manufacturers don't want to accept the perceived potential liability of saying I can use a general purpose (non-CID2 rated) transformer in a CID2 area, but if the code does not prohibit it, then why is it a concern for them?
 
If your classification requires you to limit surface temperatures lower than that as a potential ignition source, it might be an issue, but CID2 does not, yes?

Sent from my XT1585 using Tapatalk
 
If your classification requires you to limit surface temperatures lower than that as a potential ignition source, it might be an issue, but CID2 does not, yes?

Sent from my XT1585 using Tapatalk
The restriction certainly isn't in Section 501.100(B). If there were one, it would be in Section 500.8. Dig for it.
 