Johnny Bravo
Member
- Location
- Texas, United States
I'm trying to determine if installing a 45kVA General-purpose low-voltage dry-type 3-ph transformer (such as the SquareD EX45T3HCU) in a Class I, Division 2 (Groups C&D) would be a code-violation. The transformer is a 480V delta primary, with a 208Y/120V secondary.
NEC 2011 501.100 (B) points to 450.21 through 450.27.
Using the 45kVA transformer that I linked, 450.21 seems to indicate that there is no restriction as long as my transformer is "completely enclosed, with or without ventilating openings". I do not read this as being a sealed encapsulated transformer, but I could be wrong. Would you say that the linked transformer does not violate the code, and therefore can be installed in a Class I, Div 2 area?
I have asked a couple of major electrical manufacturers this question and received their answer, but I don't want to overly bias the conversation before hearing your thoughts.
Thanks.
NEC 2011 501.100 (B) points to 450.21 through 450.27.
Using the 45kVA transformer that I linked, 450.21 seems to indicate that there is no restriction as long as my transformer is "completely enclosed, with or without ventilating openings". I do not read this as being a sealed encapsulated transformer, but I could be wrong. Would you say that the linked transformer does not violate the code, and therefore can be installed in a Class I, Div 2 area?
I have asked a couple of major electrical manufacturers this question and received their answer, but I don't want to overly bias the conversation before hearing your thoughts.
Thanks.