I have been trying to locate direct language in the NEC that allows for the use of unclassified wiring techniques for thermocouples in a Class 1 Division 2 location. The only thing that I can see as an option is to consider the circuit as non-incendive to qualify.
Background:
1) Our thermocouples use simple quick-disconnect plastic heads
2) We use ordinary thermocouple extension wire out of the wire trays to connect to these thermocouples
3) Our data acquisition system is rated Class 1 Division 2
Code:
Using NEC 2014
This type of thermocouple (non-amplified, no transmitter) I believe falls under a 'simple apparatus' definition that does not need to be listed, and allows them to be connected in a non-incendive field wiring circuit.
An exemption to Article 725.121 (A) allows the thermocouple to not be listed as a Class 2 power source.
I believe Class 1 Division 2 wiring techniques only consider 'Normal' operating conditions (open, short or grounding of wiring), without the added protection from equipment faults (abnormal conditions) from our data acquisition system. The fact that the thermocouple wiring is connected to a PLC should not require the added fault protection of an IS barrier.(?)
Question:
Is our wiring technique acceptable based on NEC?
Could the absence of a formal 'control drawing' for this common scenario be the only reason for non-compliance?
Can documentation or certifications be referenced from third parties or consultants that makes this practice defensible?
Background:
1) Our thermocouples use simple quick-disconnect plastic heads
2) We use ordinary thermocouple extension wire out of the wire trays to connect to these thermocouples
3) Our data acquisition system is rated Class 1 Division 2
Code:
Using NEC 2014
This type of thermocouple (non-amplified, no transmitter) I believe falls under a 'simple apparatus' definition that does not need to be listed, and allows them to be connected in a non-incendive field wiring circuit.
An exemption to Article 725.121 (A) allows the thermocouple to not be listed as a Class 2 power source.
I believe Class 1 Division 2 wiring techniques only consider 'Normal' operating conditions (open, short or grounding of wiring), without the added protection from equipment faults (abnormal conditions) from our data acquisition system. The fact that the thermocouple wiring is connected to a PLC should not require the added fault protection of an IS barrier.(?)
Question:
Is our wiring technique acceptable based on NEC?
Could the absence of a formal 'control drawing' for this common scenario be the only reason for non-compliance?
Can documentation or certifications be referenced from third parties or consultants that makes this practice defensible?