General Use Switch?

Status
Not open for further replies.

tom baker

First Chief Moderator
Staff member
Article 100 of the NEC has the following definition for a General Use Switch:
Switch, General-Use. A switch intended for use in general distribution and branch circuits. It is rated in amperes, and it is capable of interrupting its rated current at its rated voltage.
Can someone give me an example of a general use switch? It suspect I am overlooking the obvious...
 

jtb

Senior Member
Location
Pennsylvania
Re: General Use Switch?

I agree with Hurk, any type of wall switch, or snap switch variations. Think of the bins at Home Depot.
 

tom baker

First Chief Moderator
Staff member
Re: General Use Switch?

There is a definition for a general use snap switch, its as you describe. Thats why I am curious as to what a general use switch is.
A general use snap switch is designed to mount on a device box.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: General Use Switch?

Look at 404.13(C) General use switch seems to mean a knife (disconnect) switch rated less then 1200 amps at 250 volt or less then 600 amps at 251 to 600 volts

They talk about snap switches in 404.14

Bob
 

vanwalker

Senior Member
Location
lancaster
Re: General Use Switch?

ul general info whitebook 2002, page 116, has some stuff to say about this topic, it is a very good reference.
 
Status
Not open for further replies.
Top