I am currently designing a Type I, Essential Electrical System for a ambulatory surgery center. I am following NFPA 70 & NFPA 99. My question concerns an outdoor generator in a sound attenuated enclosure.
There are 6 items that the generator needs: (1) a Receptacle, (2) Task illumination, (3) a battery charger for the battery backed-up task immumination, (4) Block heater, (5) Battery Charger, & (6) Battery Warmer.
The items that I know must be on the Life Safety Branch are: receptacle, task illumination, task illumination charger.
I am unsure about the other items. The NEC says the battery charger must be on emergency power, but NFPA 99 prevents any other loads besides their listed criteria on Life Safety or Critical.
I am unsure how to proceed with those items.