You are NEVER going to get out of the 25 ohm thing. It's in the contract. There are scenarios where it is a safety issue, so I have found it best to think of it in those terms. Just keep saying the Yes, the grounding is important but we still have to pull the required EGC. I have found it easiest to run an "external" EGC ran with the circuit conductors.
But back to the resistance testing. If you guys, like us, use a clamp on meter to check the resistance you are not checking much. Read the manual, it's for a utiltity-fed system. If you drive two ground rods connect a wire between them and clamp that thing on it will check the resistance between those two rods. I don't know what that tells ya. To check a single rod you need to use a different tool. (3-point tester). I would suggest you contact the engineers and tell them your dilemma with getting the 25 ohms, If they want it I say they design it.
I think whenever those testers register a "good" reading there is a closed loop system, ie: the ground wire is connected to the fuel tank twice or in a "loop" of some sort and the meter simply reads the resistance of the wire/steel in that loop. I highly doubt there is a single ground resistance test done that means anything in all of theater. Just my opionion