I am doing a pump station design with a generator to back up two 200hp pumps. Both pumps will not start at same time. My calculation for sizing the generator is listed below
FLA of 200hp pump (460v) (table 430.250): 240A
LRA of 200hp pump (460v) (table 430.251B): 1450A
The total starting current is 240+1450=1690A
The total starting KVA is 1690A x 480V x 1.732 = 1405 KVA
The total KW is (240 + 240) x 480 x 1.732 = 399 KW
So I have to select a 400 KW generator with at least 1450 starting KVA. Am I right?
Any thought about fuel tank? We will put a 24 hours back up fuel tank. Which code talk about the location of fuel tank?
Thanks.