A customer wants a manual transfer switch installed to provide an input / switch for backup power for a 480 V wye service. They already own a generator which is currently at a different site, and would like to utilize that. I'm still waiting on details about the generator itself, but for now, I'm assuming it's a 480 V wye generator (don't know the ground / neutral bond status of the generator yet).
The existing service from the meter into the fused main disconnect has 5 incoming wires - 3 lines, a neutral (taped white), and a small green-insulated ground wire. The incoming neutral and insulated ground are bonded together with an earth ground inside the disconnect. From the load side of the main disconnect, there are two feeds: first is 3 lines and a neutral feeding a fused surge protective device that's mounted on the side of the main disconnect; second feed is 3 lines, a neutral, and a ground feeding a 100 A, 3-pole main breaker with a neutral lug at the side of the breaker. All equipment on the system is fed from that breaker. The neutral ends at the lug in that main breaker and is not used for any equipment on the circuit.
I would like to put the manual transfer switch between the load side of the main disconnect and line side of the 100 A main breaker. Since the neutral ends at the lug in the 100 A main breaker and isn't used anywhere on that circuit, can I remove the neutral between the main disconnect and 100 A main breaker and then treat it as a 4-wire system (3 lines and a ground) for the generator / transfer switch, with no neutral connections inside the transfer switch? I would like to do this so that a 4-wire cable and 4-pin IEC pin / sleeve connector can be used to supply power from the generator to the transfer switch.
If this is allowable, what is the proper way to handle the neutral from the 480 V wye generator?
Here's a link for photos of the fused main disconnect and 100 A main breaker connections for reference:
Main Disconnect and Breaker
Thanks in advance for your time and advice.
The existing service from the meter into the fused main disconnect has 5 incoming wires - 3 lines, a neutral (taped white), and a small green-insulated ground wire. The incoming neutral and insulated ground are bonded together with an earth ground inside the disconnect. From the load side of the main disconnect, there are two feeds: first is 3 lines and a neutral feeding a fused surge protective device that's mounted on the side of the main disconnect; second feed is 3 lines, a neutral, and a ground feeding a 100 A, 3-pole main breaker with a neutral lug at the side of the breaker. All equipment on the system is fed from that breaker. The neutral ends at the lug in that main breaker and is not used for any equipment on the circuit.
I would like to put the manual transfer switch between the load side of the main disconnect and line side of the 100 A main breaker. Since the neutral ends at the lug in the 100 A main breaker and isn't used anywhere on that circuit, can I remove the neutral between the main disconnect and 100 A main breaker and then treat it as a 4-wire system (3 lines and a ground) for the generator / transfer switch, with no neutral connections inside the transfer switch? I would like to do this so that a 4-wire cable and 4-pin IEC pin / sleeve connector can be used to supply power from the generator to the transfer switch.
If this is allowable, what is the proper way to handle the neutral from the 480 V wye generator?
Here's a link for photos of the fused main disconnect and 100 A main breaker connections for reference:
Main Disconnect and Breaker
Thanks in advance for your time and advice.