Does anyone know if a wooden deck attached to a structure with combustible walls (house) is considered one structure as far as meeting the requirements of NFPA 4.1.4? The way I read it is a deck does not have walls unless it is considered as part of the house structure. I'm installing a Generac water cooled standby generator as close as possible to a wooden deck attached to a house. The water cooled units as far as I know have not been independently listed to meet the 1 hour fire rating as the air cooled units have.

Background:
Subsection 4.1.4 of NFPA 37 reads as follows: ?4.1.4 Engines Located Outdoors. Engines, and their weatherproof housings if provided, that are installed outdoors shall be located at least 1.5 m (5 ft) from openings in walls and at least 1.5 m (5 ft) from structures having combustible walls,
A minimum separation shall not be required where the following conditions exist:

(1) The adjacent wall of the structure has a fire resistance rating of at least 1 hour.
(2)* The weatherproof enclosure is constructed of noncombustible materials and it has been
demonstrated that a fire within the enclosure will not ignite combustible materials outside the
enclosure.?
 
The deck is combustible, so according to most generator manufacturers with 1hr rated enclosures the distance from the deck would be a minimum 18 inches.
just as if it were next to a combustible surface on a house.
 