beaucephas
Member
I have a situation I am trying to figure out. There is a building (3ph-4w-277/480V) with a standby generator and 3-pole ATS. The ground and neutral are not bonded at the generator. The frame of the generator is connected to a ground ring that surrounds the building and is connected to the building service. There is an equipment grounding conductor from the generator to the ATS, and one from the service to the ATS. There are four wires plus ground from the service to the ATS, but only three wires plus ground (neutral is run but not connected) from the generator to the ATS. Why would someone do this? It seems like it would create a fault. Obviously the remedy is to connect the neutral from the generator to the ATS, but I just want to make sure I am not missing something.
Is a generator considered separately derived if connected to the same ground ring as the electric service?
Thanks for your help.
Is a generator considered separately derived if connected to the same ground ring as the electric service?
Thanks for your help.