I want to make sure I have this understanding. The GFCI on the generator trips when I connect the generator to the house electrical system because the neutral is bonded to the frame and the neutral is bonded at the service.
So in order to have this portable generator to work with the house electrical system is to remove the bonding and ONLY use the generator when it is connected to the house electrical system. Because with a 4 conductor cable if the frame is energized the breaker on the generator will trip because at the service the neutral is bonded.
Am I correct or I am way off?
Thank you for your replies.
So in order to have this portable generator to work with the house electrical system is to remove the bonding and ONLY use the generator when it is connected to the house electrical system. Because with a 4 conductor cable if the frame is energized the breaker on the generator will trip because at the service the neutral is bonded.
Am I correct or I am way off?
Thank you for your replies.