Generator bonding

Status
Not open for further replies.

JoeNorm

Senior Member
Location
WA
Meter and first means and disconnect at the street, so main panel in the house has floating neutral.

If I want to supply the main panel with a generator and interlock how do I bond the generator? Four wire feed with G_N bond at unit?

thanks
 
Neutral not bonded at the generator, EGC connected to the generator.
 
So when I switch the interlock and run the Gen there would be no neutral-ground bond anywhere?
 
With a remote main like described here, I am going to install the generator as a separately derived system and use a transfer switch that switches the neutral. Generators have a very hard time supplying enough current to operate in the instantaneous trip range of the OCPD, the the extra length in the fault clearing path if the generator is a non-separately derived system makes that issue worse.
 