Bjenks
Senior Member
- Location
- East Coast of FL
When sizing the feeder breaker for multiple motors you size it at the largest motor breaker plus the FLA of the other motors, then next size down. What if you have a generator feeding this through an ATS that shuts down half the motors upon power failure. Do you size the generator feeder breaker the same size as the utility service breaker since the largest breaker size is physically the same or do you size it hypothetically on what all the circuit breakers sizing would be if those motors were not there? I am trying to see if I can lower the breaker size and conductor for the generator feed.