I would say if the 1600 and 450 amp breakers are the only overcurrent protections devices associated with the output of the generator, they are oversized.
There's nothing to limit an overload of the output windings of the generator at that combined total.
If the generator has overcurrent protection integral or ahead of the 1600 and 450 amp breakers to protect the generators output winding, then, the generator is protected and the 1600 and 450 amp breakers are not oversized,
However,
You wouldn't be able to run the 1600 and 450 amp equipment at its full capacity since the output protection of the generator's secondary is limited to roughly 1100 amps.
If you want to run your 1600 and 450 amp load at their full capacity and use them to protect the windings on the generator, you need a larger generator.
If you want to run your 1600 and 450 amp loads at the calculated load of 1089 amps for any length of time, you can roll the dice, with a protected output winding at 1100 amps, but, in my opinion, your generator is still too small.
If you want to burn your 400kw generator up, leave the 1600 and 450a overcurrent protection as the generators only overcurrent protection and let your calculated load fluctuate and exceed the generators output for a little while.
JAP>