Generator breaker sizing
hhsting
Glen bunie, md, us
Junior plan reviewer
Attached shows 400kw, 208v, three phase generator. Their are two breakers 150A and 600A shown. From one of the breakers it feeds distribution switchboard and another breaker feeds fire pump.
Would this sort of arrangement be allowed by NEC 2017 Section 700 or not for emergency generator?
And you should have your plan submitter show documentation that nat gas is allowed as a fuel source for em gen
Before you waste everyone's time here answer Gus's question. Now, considering PE' s have some level of technical writing skills you really need to learn the difference between there and their.
Roger
The basic concept, a Generator set as emergency power, is, of course allowed by Art 700.
The engineer has his work set out for him, tom's point + assuring generator OCP (445.13), and most lilely some load shedding especially with a fire pump involved.
Although most engineers tap the fire pump ahead of the main on the generator, and call for load shedding as Augie mentioned, I had a fire inspector say the generator is not held to the same standard as utility, and does not have to supply locked rotor or oversize the breaker. He said it only had to start and run the pump along with any other loads that were not shed. He gave me the section number, and I looked it up, and he appeared to be correct. But danged if I can remember the number.
Nothing wrong with that design. I would have done it that way myself (mostly). I agree with hillbilly's inspector; generators don't have to carry fire pump locked-rotor current like the utility service does.
Also, in their design there, they're leaving a lot of capacity on the generator. 400 kW @ 80% pf is 500 kVA, which at 208v can put out 1390A. The generator may be oversized if they selected it to carry the fire pump locked-rotor. All the major generator manufacturers offer sizing software and they all know how to handle a fire pump. It won't sustain the locked rotor amps, but it does provide enough voltage during starting - even without load shedding if you size it right.