hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 500kva generator with 480V three phase. There are two breakers at generator provided one is 600A and another is 200A. The generator has internal overload protection.
600A breaker has 600A cable
200A breaker has 155A cable size feeds motor load only
So generator
Full load is 601A.
601x1.25=751A next standard size is 800A.
Would those breaker be correct size or too large? Reason is i dont find anything in 445, 700,701 NEC 2017.
600A breaker has 600A cable
200A breaker has 155A cable size feeds motor load only
So generator
Full load is 601A.
601x1.25=751A next standard size is 800A.
Would those breaker be correct size or too large? Reason is i dont find anything in 445, 700,701 NEC 2017.