I have 350kW generator 480V three phase that has one 400A breaker and another 600A breaker. 400A feeds optional standby and 600A feeds emergency branch and fire pump. Fire pump is 30HP at 480V three phase.

My question is their anything in NEC 2017 that regulates or says in regrading the above type generator breakers sizing? Aren’t they oversized?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
445.12 requires the generator have overcurrent protection. It is highly probable that yours will have overloadm protection by inherent design.
 

Birken Vogt

Senior Member
Location
Grass Valley, Ca
The generator is sized to the calculated load by various factors.

The breakers on the generator are sized to protect the wires they are connected to in accordance with the NEC for wire size

The generator was probably custom ordered with those size breakers to fit the application. What do the plans and engineering say?
 