I have a 100kW generator that I am going to order and have a question on the sizing of the output breaker.
What does the generator manufacturer go by to size the output breaker?
I see in 2008 NEC 445.13 the wire from the generator terminals to the breaker need to be sized at 115% of the rated output.
I don't see how they size the output breaker though.
This particular generator is 100kW at 480 volts. The output is 150 amps and the breaker is going to be 175 amp.
If it was 125% of the output then it would be 187.5 amp.
I would have rounded up to 200 amp per 240.4 (B).
How does the generator supplier size this breaker.
Is it specified by the NEC or their own criteria?