Attached emergency generator supplies fire pump and panel GEN. Panel GEN feeds life safety ATS, Legally optional standby and Optional ATS.
The generator is 400kW at 408/277V three phase with full load amps of 481A. The generator breakers 150A and 600A is there anything in NEC 2017 to size them? Are they correct or incorrect size?