I have a situation where a generator has an 150A breaker which feeds a #2 AWG cable going to a transfer switch. On the load side of the ATS the cable is #2/0 and it terminates into a 100A breaker in a panel. Distance between generator breaker and 100A breaker in panel is about 20ft.
I know the #2 cable is not protected by the 150A gen breaker per 240.4(B) however can it be protected by the 100A breaker in the panel but one of the provisions of the tap rule?
I know the #2 cable is not protected by the 150A gen breaker per 240.4(B) however can it be protected by the 100A breaker in the panel but one of the provisions of the tap rule?