Generator cable for residential home standby generators is available with 3 #3 awg copper and 6-#16 awg copper control wires.
When the generator is not running, 3 control conductors are energized with AC current, plus a neutral, and there is 12 volt DC on two other conductors.
When the generator is running the two #3s are energized, plus the neutral, and other than briefly at start up, only one #16 is energized.
The 26 kw generator has a 110 amp main breaker.
Considering all factors, is this generator cable legal to use with a 26 kw unit?
When the generator is not running, 3 control conductors are energized with AC current, plus a neutral, and there is 12 volt DC on two other conductors.
When the generator is running the two #3s are energized, plus the neutral, and other than briefly at start up, only one #16 is energized.
The 26 kw generator has a 110 amp main breaker.
Considering all factors, is this generator cable legal to use with a 26 kw unit?