I am currently in India helping a friend to wire his house to IEE standards (UK).
The design current (before diversity) is approximately 170 amps across the three phases, with only one intermittent three-phase load of 5hp for the water purification system and pumps.
The real life load is likely to be less than 15 amps per phase (single phase loads) in total.
We ordered a 30kva 230v 3-phase generator (24kw) for standby purposes, which is only for the house supply, excluding water treatment, all pumps and A/C units.
The suppliers originally stated that we required a 100kva DG set for this small house, but we established that they were wrong ... the actual size that would suffice is 20kva, but we uprated to 30kva to provide overhead.
They now demand that we supply 3.5 core 50mm SWA for connection to and from the 30kva DG set, which appears to me to be completely wrong.
I know very little about generators and my research on the web has indicated that 16mm cross section is more than sufficient, however, we were going to supply 25mm four-core SWA anyway.
Some advice on the real cable requirement would be appreciated.
My thanks
Grahamb
The design current (before diversity) is approximately 170 amps across the three phases, with only one intermittent three-phase load of 5hp for the water purification system and pumps.
The real life load is likely to be less than 15 amps per phase (single phase loads) in total.
We ordered a 30kva 230v 3-phase generator (24kw) for standby purposes, which is only for the house supply, excluding water treatment, all pumps and A/C units.
The suppliers originally stated that we required a 100kva DG set for this small house, but we established that they were wrong ... the actual size that would suffice is 20kva, but we uprated to 30kva to provide overhead.
They now demand that we supply 3.5 core 50mm SWA for connection to and from the 30kva DG set, which appears to me to be completely wrong.
I know very little about generators and my research on the web has indicated that 16mm cross section is more than sufficient, however, we were going to supply 25mm four-core SWA anyway.
Some advice on the real cable requirement would be appreciated.
My thanks
Grahamb