I have separately derived generator that has no main breaker. Conductors call it A from the generator to the first overcurrent protection are 25 feet apart. I know the equipment grounding conductor is same as supply side bonding and size it per Table 250.102(C)(1).
However I have the following questions:
1. I dont see phase and neutral of Conductors A to be service conductors since they are not from utility. I dont see them as being feeders either since between generator and first overcurrent protection there is no overcurrent protection. How do you size phase and neutral Conductors A? Its confusing. Their is nothing like this 240.21 for generator.
2. Does NEC 2017 require mandatory to have generator main breaker at the generator? If yes then where is it in code.
Thank you
However I have the following questions:
1. I dont see phase and neutral of Conductors A to be service conductors since they are not from utility. I dont see them as being feeders either since between generator and first overcurrent protection there is no overcurrent protection. How do you size phase and neutral Conductors A? Its confusing. Their is nothing like this 240.21 for generator.