Davids1964
Member
- Location
- Virginia
I am working on a 14 yr old generator that keeps tripping at the shunt trip mechanism. The 2000amp breaker has been replaced along with a new trip unit. It still keeps shutting down with only have the capcity load (750amps). The generator is a 15KW 480V with 5 sets of 500mcm wire to the switch gear. Switch gear only 5 ft away.The wire has been megged. An engineener is saying the wiring is under rated. I would like to know if he is correct on that issue. We also had a representaive from the manufacture of the breaker come out to look at the breaker. Yes, we have addressed vibrations also. Has anyone ever ran across a situtaion as this. The generator is a Steward Stevenson. Any help would be appreicated.