We have supplied a 2 sets 1145kw Generator sets with 1700 amps rated current ,480 Volts that is being paralleled and stepped up to 4160 Volts 5MVA Transformer delta wye connected supplying a medium voltage 4160 V softstarter driving a 600 Kw motor .
The Generator runs in parallel using a micro proccessor based generator auto synchronizer(Woodward EGCP2) without load, however , when we try to start to load the 600 Kw Motor , the generator circuit breakers trip off suddenly without any fault display in our generator controler.
We repeat the sequence operation, but this time we have disable the instantenous trip of the circuit breaker ,unfortunately same tripping trouble occured.
My question does the presence of harmonics affects the operation of the generator controller?
Is my 2 x 1135 kw, 480 v Generators in parallel is not enough to start the 600 Kw motor with a starting current of 2890 Amperes?
Do i have to install a NGR at transformer secondary.