AZElectrical
- Arizona
I have an installation where a 480V standby generator is equipped with four breakers. Three of these are for feeds to the emergency side of transfer switches and one is for a load bank. The circuit breakers are mounted on the machine, high off the ground (well over 6'-6", I don't know the exact height). The generator frame and breakers are inside an enclosure which is on top of a belly tank, the door of which must be opened to gain access to the breakers and generator control panel.
The breakers are certainly not readily accessible as required in 240.24(A) -- currently there is no permanent method to reach the handles. Reading through 445, however, I do not see anything that indicates generator breakers need to be readily accessible. Currently people are using a roll away step ladder with hand rails when they need to gain access to the breakers or control panel.
I am struggling to determine if this installation is code compliant. Is the height of the breakers a code violation? If it is, I do not know how we will be able to resolve the issue as there isn't much room in the area beneath the breakers. Thank you for any input.