Is there any calculation I can perform to determine what circuit breaker should be installed at the generator? The generator is diesel 80KW 277/480. Or should I just rely on what the manufacturer says? I thought it would be 80000= 1.732 X I x 480 and solving this I get I=96 Amps. Should I use a 100A circuit breaker to prevent damage to the generator or should I do 125% * 96Amps => 120A and thus use a 125A circuit breaker? The generator manufacturer stated it would come with a 125A circuit breaker but I'd like to know how they came up with this calculation.