Customer purchased 14kw Generac some time ago. Thought he would do it himself. He has main panel with a sub
next to it. Each with circuits to be switched to generator. I'm mounting generator transfer switch next to these.
I've read 312.8 and it seems legal to connect the generator circuit whip to the adjacent panel (main) and pass the
other generator circuits through to the other panel (sub).
This should be ok. Otherwise I would need to separate the generator circuit into 2. The original whip, and a 3/4"
raceway to the sub.