H hou628 Member Apr 6, 2015 #1 A client in the New York area wants to install a new generator right next to an existing ATS. Is there a clearance requirement between the Generator and ATS that needs to be satisfied?
A client in the New York area wants to install a new generator right next to an existing ATS. Is there a clearance requirement between the Generator and ATS that needs to be satisfied?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Apr 6, 2015 #2 See Section 110.26, review and reply if you have any questions.
iwire Moderator Staff member Location Massachusetts Apr 7, 2015 #3 I agree with Tom and will add that you must also maintain the clearances indicated by the installation instructions.