Hypothetical.
I have a large generator, it has a 400 amp breaker on it.
I installed it about 75' behind my home and ran an underground raceway from the genset in through the foundation directly into the back of a 100 amp fused disconnect.
My calculated load is 95 amps total continuous and non-continuous.
I ran 3 AWG CU XHHW-2 from the 400 amp genset OCPD all the way to the 100 amp fused disconnect inside.
Do I pass inspection or get a red tag.
Remember red tags come with code sections attached.