Dennis Alwon said:What part of 240.21(B)(5) does this not comply with???
IMO my made up installation compiles completely with 240.21(B)(5). :smile:
Dennis Alwon said:What part of 240.21(B)(5) does this not comply with???
Dennis Alwon said:My denseness is overwhelming me.
chris kennedy said:Don't feel bad. I caught a wicked case of that as well.
Well we REALLY don't know that for sure. You said an"Underground Raceway." How do we know you complied with the NEC in an underground installation. You might have run those condutors in ENT thinking we might not notice. Well? fess up!:grin:iwire said:IMO my made up installation compiles completely with 240.21(B)(5). :smile:
I don't think there is one. I hadn't read the def of Tap Conductors in so long I assumed it said splice or something similiar.Dennis Alwon said:Good now I feel better but where is the violation?
This IMO is huge given my EE's don't apply this.from the 08
Tap Conductors. As used in this article, a tap conductor is defined as a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4.
iwire said:Hypothetical.
I have a large generator, it has a 400 amp breaker on it.
I installed it about 75' behind my home and ran an underground raceway from the genset in through the foundation directly into the back of a 100 amp fused disconnect.
My calculated load is 95 amps total continuous and non-continuous.
I ran 3 AWG CU XHHW-2 from the 400 amp genset OCPD all the way to the 100 amp fused disconnect inside.
Do I pass inspection or get a red tag.
Remember red tags come with code sections attached.![]()
frenchelectrican said:i was going say it is ok as long you used the tap rules but somehow i just can't find the tap rules related to underground conductors.
Merci,Marc
Where did you go out? I was out at Blacks in SD today 1-3 NW. oops off topic.The Iceman said:I spent 5 hours today studying commercial calculations and the rest of the day surfin some beautiful clean waves. It's getting late and I'm having a case of the denseness as well. Mr. iwire I give up is their a code violation or not?