So I have a 1.5 meg generator feeding a switchgear. At the generator I have a 2500 amp 600 volt breaker. Per plans we have installed 8 parallel runs of 3x750mcm and a 350mcm ground copper in 4" coated rigid in a underground concrete in cased duct bank. The conduits stub up in the bottomless enclosures so I have no metal contact to any of the raceways. Due to the overcurrent protection rating I need a 350mcm bonding conductor to bond the raceways, however I have been unable to find a bonding bushing with a lug on it bigger than 250mcm. I am also under the impression to change the lugs on the bushings would destroy the UL listing of the bushing. Any suggestions or is there something I am misinterpretating?