Please see responses in red to each question below:My questions:
1. What are the ratings of the two transfer switches?
2. What is the rating of the breaker within the MDP that supplies the first ATS?
3. Do I infer correctly that point 21 is fed from the MDP?
4. If that is a "yes," then what is the rating of the breaker that supplies point 21?
5. Why did you choose a 3 pole ATS?
My comments (taking note that we do not know how far along the design process is at this time, so some of these comments may be too early):
1. You have a generator rated at 750 KW (937 KVA at 0.8 pf). That gives you about 1130 amps. Yet you are feeding 2000 amps worth of ATS with it. This is a mismatch.
2. The right hand ATS is supplied without any overcurrent protection.
3. Even if the left hand ATS is fed by a fused disconnect (I don't have your list of symbols), the feeder to that disconnect has no overcurrent protection.
4. If the two disconnects are fused, then you should show the fuse ratings.
5. You are not showing the ratings of the two ATSs.
6. You are not showing any conductor sizes.
My answer to your question:
A disconnect should be sized at or above the calculated load it is intended to serve. If it is fused, the fuses should be sized to protect the conductors and the component immediately downstream. For example, the fuses in disconnect H8 must be able to protect transformer T8 and its primary conductors.
What is "17" ?
Any thoughts on my responses in red above would be appreciated. I was hoping charlie b would respond to my comments.Got it (I'm used to pads being utility fed and just realized HB is feeding the transformer)![]()
I agree with charlie that the feed to the 1600 amp ATS from the generator needs a disconnect/overcurrent device and you need to assure H10 is fusible.
also I assume the "420" amp breaker is actually a 400 amp based on the ATS rating.
I will be upsizing the Generator to support the load (this will be in my new revision set). As far as the generator protection, you are right some sort of fusible or circuit beaker would need to support the OCPD. Outside of just adding a fusible disconnect switch is between ATS and generator is there anything else i can do? Also do i need to have both ATS to a 4 pole instead of a 3 pole?Unless there is OCP at the generator you need to protect the conductors and the ATS on their supply side.
There still remains a problem in that H8 and H10 (1600 + 400) ratings excess the output capacity of the generator (1130). How is generator protection addressed.
What Code section requires protection of the ATS on the supply side?Unless there is OCP at the generator you need to protect the conductors and the ATS on their supply side.
Interesting question.. Is there any equipment, other than service, rated that doesn't need line side protection ?What Code section requires protection of the ATS on the supply side?
In solar...690.9(A)(1) conductorsI can't imagine a situation where conductors with no OCP would be allowed to enter a structure without immediate OCP.
That is a special case where a dead short can go on indefinitely with no ill effects.In solar...690.9(A)(1) conductors
That is a special case where a dead short can go on indefinitely with no ill effects.
It could be argued that the 115% generator rule is similar, but I never see it used in practice. I am not sure what it is supposed to accomplish.
Thank you all for discussing my one-line connection. I have incorporated all your suggestions above. The only question I have is, is there a requirement that suggests adding an OCPD (fusible disconnect switch) between the ATS and generator?In solar...690.9(A)(1) conductors