Re: generator connections
This is where I am having a problem understanding the definition of a service panel.
Are you saying that when a transfer switch is added on the supply side of a service, the transfer switch becomes the service panel?
You say a panel can't be grounded with the neutral. The service panel is grounded by the neutral.
I don't think the transfer switch changes the definition of a service panel.
There is no such thing as a sub panel. There is no words in the code that says the panel must be supplied by 4 wires and the ground and neutral must be separated.
When there is a parallel path, this procedure will correct the objectionable current problem. When there is no parallel path except the earth, I can not see any code rule that says the neutral and ground must be separated.
There is a lot of holes in the logic of grounding, this is another one. The method to prevent objectionable current flow is a result of one individuals decision.
I will drop this issue for now, it goes no where. When the NEC specifically states that a panel shall have the neutral and ground separated, even if the overcurrent device is a foot away, then I will form another opinion.