• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Generator control wiring

Status
Not open for further replies.

jim s.

Member
There is a familiar generator company that supplys a whip for connection from the transfer switch to the generator. This whip contains both power and control wiring from a class (2) transformer. Chap. 725 nec says only functionally associated equipment of a class (1) is allowed to share the same raceway with power cables. The transformer is located in the generator,and is 230/12v.and looks to be 40 or 50 watts. Any thoughts or is this manufactured whip exemp.


jim s.
 

DGrant041

Senior Member
Location
Peoria, Illinois
Jim-

Manufr's whip is exempt.

Code:
725.1 Scope
This article covers remote-control, signaling, and power-limited circuits
[B]that are not an integral part of a device or appliance.[/B]

I believe someone posted a similar question recently. You may try searching the forum posts for that familiar generator company's name. ;)
 
Status
Not open for further replies.