generator cord set

Status
Not open for further replies.

Mr.MOD

Member
i will be installing a interlock kit (k-8110) to a ge singlephase load center with a pb30 at the remote loc for the generator cordset. however the generator is an older coleman w a 120v/15a(5-15R) duplex and 240v/20a
(6-20R)duplex. i havent checked the voltage between the 2 15a to see if there is 220 available or the n-g bond on the generator at this time but of course will do so before applying a load. my question is, have any of the pro's (members of MHF)seen or used this type of cord set
http://nooutage.com/adapt-y.htm ? or should i advise the h/o to seek out a newer generator the generator is a coleman power base 5000.
 

iwire

Moderator
Staff member
Location
Massachusetts
In my opinion, this cord set

adaptor-wye.jpg


will violate 406.6(B).

Once in use if you unplug one of the 5-15Ps the prong will be live from a back feed through the loads.
 

Mr.MOD

Member
if 1 5-15 became unpluggedfrom the generator wouldnt that disconnect that phase on the load center leaving just 1 phase powered.
so backfeed could occur from the 220 loads?
 

Mr.MOD

Member
with that in mind i see no use for this product
I'll advise the h/o the current generator is insufficient for the application and could be used as a ext cord supply to individual loads
Ty for the replies
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The equipment the panel supplies is going to run a bit funky without a neutral.
Ah, a 6-20 is 240v and EGC only?

Okay, if the genny circuitry includes a neutral, how about adding a 120/240v + EGC receptacle?

How about the receptacle configuration in Bob's pic? Is that an L-20R?
 