I thought that the OCP at the generator had to be service entrance rated or else another rated OCP would be required before entering the building: could you clarify this?
Q12. We have a standby generator with a circuit breaker mounted on the generator and an automatic transfer switch installed on the load side of the service disconnect. Is an additional disconnecting means required for the generator feeder conductors entering the building?
A12. Where an outdoor-housed generator is equipped with a readily accessible disconnecting means located within sight (within 50 ft) of the building or structure, an additional disconnecting means isn?t required on or at the building or structure for the generator feeder conductors that serve or pass through the building or structure [700.12(B)(6)].
acdcmontana May 31 2007, 7:34 pm EDT
Reply from: Mike Holt
There is no such rule to require the generator disconnect to be service rated. Sorry.