m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Oct 12, 2020 #1 I am referring to 445.18(A), where disconnecting mean is required for generator shutdown, per Handbook the disconnecting mean is not a breaker But, by referring to Mike Holt illustration the disconnecting means seem like breakers, is it just a graphic mistake?
I am referring to 445.18(A), where disconnecting mean is required for generator shutdown, per Handbook the disconnecting mean is not a breaker But, by referring to Mike Holt illustration the disconnecting means seem like breakers, is it just a graphic mistake?
tortuga Code Historian Location Oregon Occupation Electrical Design Oct 18, 2020 #2 445.18 is just saying you need a disconnect. There is nothing in 445 or 700 that says it cant be a OCPD. 445.12 deals with overcurrent protection. They don't need to be the same device, but they can be.
445.18 is just saying you need a disconnect. There is nothing in 445 or 700 that says it cant be a OCPD. 445.12 deals with overcurrent protection. They don't need to be the same device, but they can be.