• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Generator Engine Runs Fine but No Voltage is Produced.

Status
Not open for further replies.

Saturn_Europa

Senior Member
Location
Fishing Industry
Occupation
Electrician Limited License NC
I have an FG Wilson back up genset at my house. Its brand new and the unit has never had any problems. Last night there was a lightening strike on a utility pole about 20 meters away. The genset will run fine for 30 seconds then throws the alarm: u L. Its a shutdown alarm.

It is producing around 23 volts L -N and 45 v L -L. Its a 230/400 v 3 phase machine.

I think its the exciter. Anyone else?

Please see attached data plate.
 

Attachments

  • photo22176.png
    photo22176.png
    71.7 KB · Views: 2

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I have an FG Wilson back up genset at my house. Its brand new and the unit has never had any problems. Last night there was a lightening strike on a utility pole about 20 meters away. The genset will run fine for 30 seconds then throws the alarm: u L. Its a shutdown alarm.

It is producing around 23 volts L -N and 45 v L -L. Its a 230/400 v 3 phase machine.

I think its the exciter. Anyone else?

Please see attached data plate.

Did you field flash it to see?
 

Russs57

Senior Member
Location
Miami, Florida, USA
Occupation
Maintenance Engineer
My experience, without knowing the details, would be diodes (and surge suppressors if present) in the generator followed by voltage regulator as most likely suspects.
 
Status
Not open for further replies.
Top