I needed to give an answer and did not get any input in time. See if you agree with my response.
Someone questioned our sizing of the generator output feeder between the generator breaker and the transfer switch. Below are the code referances I cited.....See if you agree. I used the 90 degree rating of 4/0 becuase we do have 90 degree terminals on the breaker and xfer switch.
NEC 240.4 Protection of conductors indicates the conductors need to be protected in accordance with their ampacities from table 310.16. In this case 260 amps but because 260 is not a standard amp setting (see 240.6) which allows you to select the next highest standard trip setting which is 300. A 300 amp breaker is being provided with the generator.
Using the table NEC table 310.16, 90 degree C rating of the 4/0 wire it is rated for 260 amps which is 115 percent more than the nameplate amp output rating of the generator.