Quick question - do I need to treat the feed from a emergency generator like a service? A disconnect where it enters the building?
Nothing, other than a supply from the utility, is a service.I am pretty sure the feed from a generator is defined as a service. See 230.2(A).
A circuit breaker in the MDP feeds the normal side of the transfer switch.
The transfer switch (common) feeds a subpanelboard.
230.2(A) (1) - (5) act as exceptions to the main rule that says a building is only permitted to have a single service. It has nothing to do with a feeder from a generator.Service. The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served.
OK Don. So if I have an NEMA 3R breaker enclosure as an outside feeder disconnect, because the handle of the breaker is not visible, I need another disconnect?
OK Don. So if I have an NEMA 3R breaker enclosure as an outside feeder disconnect, because the handle of the breaker is not visible, I need another disconnect?
.In Sight From (Within Sight From, Within Sight).
Where this
Code specifies that one equipment shall be ?in
sight from,? ?within sight from,? or ?within sight of,? and
so forth, another equipment, the specified equipment is to be
visible and not more than 15 m (50 ft) distant from the other
225.32 Location.
The disconnecting means shall be installed
either inside or outside of the building or structure
served or where the conductors pass through the building or
structure. The disconnecting means shall be at a readily
accessible location nearest the point of entrance of the conductors.
For the purposes of this section, the requirements
in 230.6 shall be utilized.
OK Don. So if I have an NEMA 3R breaker enclosure as an outside feeder disconnect, because the handle of the breaker is not visible, I need another disconnect?
If you can see the actual disconnect enclosure, I think you are in compliance. Many generators have a generator enclosure and the disconnect is inside that enclosure and that would not be within sight.OK Don. So if I have an NEMA 3R breaker enclosure as an outside feeder disconnect, because the handle of the breaker is not visible, I need another disconnect?
CEB,
I understand that it is not a service that is why I called it a feeder disconnect. I am disagreeing with the interpretation that the disconnecting means itself must be within sight and is not permitted to be located behind a cabinet or enclosure door. Many inspectors have interpreted "within sight" to preclude the generator disconnecting means from being located within the generator enclosure. I disagree with this interpretation.
If the disconnect is outside of the building, and is serving as the required building disconnect, the disconnect itself must be within sight from the building. I think the code is clear on this issue.CEB,
I understand that it is not a service that is why I called it a feeder disconnect. I am disagreeing with the interpretation that the disconnecting means itself must be within sight and is not permitted to be located behind a cabinet or enclosure door. Many inspectors have interpreted "within sight" to preclude the generator disconnecting means from being located within the generator enclosure. I disagree with this interpretation.
The wording in 701 and 702 for legally required standby systems and optional standby systems is the same. They all clearly require the disconnect at the generator, where that disconnect is being used as the building disconnect, to be within sight from the building.700.12(B)(6) Outdoor Generator Sets. Where an outdoor housed generator set is equipped with a readily accessible disconnecting
means in accordance with 445.18, and the disconnecting means is located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure. Where the generator supply conductors terminate at a disconnecting means in or on a building or structure, the disconnecting means shall meet the requirements of 225.36.